Default need electricians assistance, GVRD [bby]

hey,

a while back i was looking for some quick connect fittings to make extension cords for my MH ballasts.

well i found some, and tried to put them together myself, and well... i did a hack job.

plugging them in trips the GFCI.

was wondering if there was an electrician among us that could help me out putting these extensions together.

of course i would compensate you, some pocket change for an easy job, or frags if i have something you want.

just let me know, thanks!
__________________
- S H A O -
Reply With Quote
  #2  
Old 08-19-2011, 12:45 PM
reefermadness's Avatar
reefermadness reefermadness is offline
Member
 
Join Date: Aug 2008
Location: Woodstock, ONTARIO
Posts: 849
reefermadness is on a distinguished road
Default

I'm not an electrician but what are the colours you are trying to match up?
Reply With Quote
  #3  
Old 08-19-2011, 01:03 PM
wingedfish wingedfish is offline
Member
 
Join Date: Sep 2010
Location: Medicine Hat
Posts: 112
wingedfish is on a distinguished road
Default

white to the silver screw, black to the copper one and green to the green one
Reply With Quote
  #4  
Old 08-19-2011, 01:39 PM
reefermadness's Avatar
reefermadness reefermadness is offline
Member
 
Join Date: Aug 2008
Location: Woodstock, ONTARIO
Posts: 849
reefermadness is on a distinguished road
Default

Quote:
Originally Posted by wingedfish View Post
white to the silver screw, black to the copper one and green to the green one
You just explained an outlet...he is trying to put two cables together I believe.

If they have the same colour wires (ie.black,white,green) than simple logic is to just match them up.....if they have different colours well than its a little more complicated.
Reply With Quote
  #5  
Old 08-19-2011, 02:27 PM
davefrombc davefrombc is offline
Junior Member
 
Join Date: Oct 2010
Location: About 10 miles east of Mission, BC
Posts: 7
davefrombc is on a distinguished road
Default

It depends on the fixture but normally the colours coming from a unit are black , white and green. If you are tripping a GFI, I suspect you have the neutral wire ( normally white and to the silver screw on a plug or socket ) and the safety ground ( normally green , but may be a bare wire in some fixtures with wires meant to go to a box rather than an extension cord) switched. Power wire goes to the bronze screw in a plug or socket on an extension cord or wall socket .
Reply With Quote
  #6  
Old 08-19-2011, 06:12 PM
smokinreefer's Avatar
smokinreefer smokinreefer is offline
Gold Member
 
Join Date: Aug 2001
Location: burnaby,bc,canada
Posts: 1,441
smokinreefer is on a distinguished road
Send a message via MSN to smokinreefer
Default

yes, the cord has black, white and green.
it's been a couple weeks since i attempted this, i'll open them up and take a look at what mess i gone done! lol.

thanks for the input. i'll get back to you guys!
__________________
- S H A O -
Reply With Quote
  #7  
Old 10-01-2011, 04:29 AM
cyberdude47 cyberdude47 is offline
Member
 
Join Date: Jul 2008
Location: Prince George
Posts: 59
cyberdude47 is on a distinguished road
Default

I'm a electrician. You can pm me with what your trying and I can try to help u out. Gfci's can trip for numerous reasons. Some ballasts leak current and can cause a premature trip. It only takes 7 thousands of a amp to trip when it sees a difference in current between the hot and neutral.
Reply With Quote
  #8  
Old 10-02-2011, 04:01 PM
smokinreefer's Avatar
smokinreefer smokinreefer is offline
Gold Member
 
Join Date: Aug 2001
Location: burnaby,bc,canada
Posts: 1,441
smokinreefer is on a distinguished road
Send a message via MSN to smokinreefer
Default

hey all,

i'm basically trying to move my MH ballasts further away.

i have 3 250W vertex ballast hooked up to a fixture. but the quick connect cords on them are pretty short, so the ballasts are sitting on a fold out sidetable right beside the tank.

to me, its a hazard, and a wiring mess. so i wanted to make these quick connect extension cords to go inbetween the fixture and ballasts so i can place them further away from the tank, and in a neat fashion.

they currently work fine connected to the GFCI with only the original cords.
__________________
- S H A O -
Reply With Quote
  #9  
Old 10-02-2011, 05:33 PM
cyberdude47 cyberdude47 is offline
Member
 
Join Date: Jul 2008
Location: Prince George
Posts: 59
cyberdude47 is on a distinguished road
Default

What type of cable are you using to extend the wiring, you have to be careful because standard nmd90 (loomex) is only rated for 300 volts and with hid lighting te strike voltage can run upwards of 400 Volts. The cable you use has the be 600volt rated sow cable (aka cabtire) would be a appropriate choice also the connectors that you use need the same voltage rating, note this is only for the secondary side of the transformer. The primary side would be ok
Reply With Quote
  #10  
Old 10-02-2011, 09:36 PM
smokinreefer's Avatar
smokinreefer smokinreefer is offline
Gold Member
 
Join Date: Aug 2001
Location: burnaby,bc,canada
Posts: 1,441
smokinreefer is on a distinguished road
Send a message via MSN to smokinreefer
Default

Quote:
Originally Posted by cyberdude47 View Post
What type of cable are you using to extend the wiring, you have to be careful because standard nmd90 (loomex) is only rated for 300 volts and with hid lighting te strike voltage can run upwards of 400 Volts. The cable you use has the be 600volt rated sow cable (aka cabtire) would be a appropriate choice also the connectors that you use need the same voltage rating, note this is only for the secondary side of the transformer. The primary side would be ok
just to clarify...
is the primary side from the wall to the ballast? secondary being from ballast to fixture?

so this is the cable i used...
300V only... so this is my problem, and the connectors might be suspect too.

oh well, learn something new everyday. there goes $50! lol.
__________________
- S H A O -
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 09:13 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.