I cannot find anything to suggest a residential meter measure kVA, only watts.

Quote:
There are three terms you will encounter when dealing with alternating (AC) power (as opposed to DC or batteries). The first is the kilowatt, abbreviated kW, and it represents real power. Real power can perform work. Power company utility meters on the side of your house measure this quantity and charge you for it.

The second term is reactive power, and it is measured in KVAR which is short for kilo volt amp reactive. Unlike kW, it cannot perform work. Residential customers do not pay for KVAR, and utility meters on houses do not record it.

The third term is apparent power, referred to as KVA. If you hook up two multimeters to measure current and voltage and then multiply the readings together, you get apparent power in volt amps, or VA. To distinguish it from real power, VA is used instead of W.
Reply With Quote
  #2  
Old 03-07-2013, 06:52 PM
mrhasan's Avatar
mrhasan mrhasan is offline
Member
 
Join Date: Jun 2012
Location: Calgary
Posts: 2,893
mrhasan is on a distinguished road
Default

Quote:
Originally Posted by sphelps View Post
I cannot find anything to suggest a residential meter measure kVA, only watts.
Yap residential meters record KWh, not KVA.
__________________

You wouldn't want to see my tank. I don't use fancy equipment and I am a noob
Reply With Quote
  #3  
Old 03-07-2013, 06:53 PM
wmcinnes's Avatar
wmcinnes wmcinnes is offline
Member
 
Join Date: Jan 2012
Location: Edmonton
Posts: 338
wmcinnes is on a distinguished road
Default

Quote:
Originally Posted by mrhasan View Post
Yap residential meters record KWh, not KVA.
Thus your meter only counts the real power.


I'm with Steve and his research.
__________________
Wayne

Rainforest of the Sea
First 90g Reef
Reply With Quote
  #4  
Old 03-07-2013, 06:55 PM
mrhasan's Avatar
mrhasan mrhasan is offline
Member
 
Join Date: Jun 2012
Location: Calgary
Posts: 2,893
mrhasan is on a distinguished road
Default

Quote:
Originally Posted by wmcinnes View Post
I'm with Steve and his research.
Then my question is, how would each of the real power of individual components in the household be calculated by the utility meter?
__________________

You wouldn't want to see my tank. I don't use fancy equipment and I am a noob
Reply With Quote
  #5  
Old 03-07-2013, 07:01 PM
wmcinnes's Avatar
wmcinnes wmcinnes is offline
Member
 
Join Date: Jan 2012
Location: Edmonton
Posts: 338
wmcinnes is on a distinguished road
Default

Quote:
Originally Posted by mrhasan View Post
Then my question is, how would each of the real power of individual components in the household be calculated by the utility meter?
They simply measure kW and not kVA.

They consist of a motor with the stator current being the current into the building and the rotor curreent being proportional to the voltage at the building input. The motor turns a disc (the disc you see rotating in the window) that passes through a magnetic field generating eddy currents in the disc and this regulates the speed at which the disc turns so that the meter can be adjusted to read correctly.
__________________
Wayne

Rainforest of the Sea
First 90g Reef
Reply With Quote
  #6  
Old 03-07-2013, 07:05 PM
mrhasan's Avatar
mrhasan mrhasan is offline
Member
 
Join Date: Jun 2012
Location: Calgary
Posts: 2,893
mrhasan is on a distinguished road
Default

Quote:
Originally Posted by wmcinnes View Post
They simply measure kW and not kVA.

They consist of a motor with the stator current being the current into the building and the rotor curreent being proportional to the voltage at the building input. The motor turns a disc (the disc you see rotating in the window) that passes through a magnetic field generating eddy currents in the disc and this regulates the speed at which the disc turns so that the meter can be adjusted to read correctly.
1. KW is not a direct unit so the meter actually does some conversions within itself

2. That is exactly how it is done. The rotor moves proportionally to the product of voltage and current to shows kWh consumption. No PF involved that's it. So when a outlet draws 1.85A @ 115V, that means the rotor is turning at a proportional rate directly to the product of those two.

The motor needs 82W to run and it is taking in 82W but due to its inefficient manner (age, water, etc.), the pump has to take in more power and hence 1.85*115V.

For this motor, you are bringing 1.85A "in" the house.
__________________

You wouldn't want to see my tank. I don't use fancy equipment and I am a noob
Reply With Quote
  #7  
Old 03-07-2013, 07:12 PM
wmcinnes's Avatar
wmcinnes wmcinnes is offline
Member
 
Join Date: Jan 2012
Location: Edmonton
Posts: 338
wmcinnes is on a distinguished road
Default

If the current and voltage are in phase, the motor speed is the product of voltage and current (PF=1). If they are not in phase the motor in the meter will run fast for part of a cycle and slower for the other part with the average speed being the product of the in-phase voltage and current. Thus measuring real power.
__________________
Wayne

Rainforest of the Sea
First 90g Reef
Reply With Quote
  #8  
Old 03-07-2013, 07:15 PM
sphelps's Avatar
sphelps sphelps is offline
Member
 
Join Date: May 2006
Location: Lyalta, East of Calgary
Posts: 4,777
sphelps is on a distinguished road
Default

According the producers of the energy monitor:

Quote:
In AC power measurements, there actually three separate power components that can be measured:

Apparent Power: Measured in VA (volt - amperes). This is measured by taking the RMS voltage and RMS current readings and multiplying them together. This is what the eMonitor reports for power. All electrical circuits must be sized to handle apparent power because instantaneously, this is the maximum amount of power that can be flowing in a circuit.

Real Power: Measured in watts. This is the actual power that is being consumed by the load. This is what the utility company measures on the meter, as is what customers see on their electrical bill.

Reactive Power: This is kind of like imaginary power. It is really the difference between the Apparent Power and the Real Power. It is power that flows back and forth while the voltage and current are out of phase and is caused by the inductive load. Your utility company does not charge for reactive power, but it must handle reactive power, and reactive power does cause real current to run in your wires, and can generate heat. Reactive power is measured in VAR (volt - amperes reactive).
Reply With Quote
  #9  
Old 03-07-2013, 07:16 PM
mrhasan's Avatar
mrhasan mrhasan is offline
Member
 
Join Date: Jun 2012
Location: Calgary
Posts: 2,893
mrhasan is on a distinguished road
Default

Quote:
Originally Posted by wmcinnes View Post
If the current and voltage are in phase, the motor speed is the product of voltage and current (PF=1). If they are not in phase the motor in the meter will run fast for part of a cycle and slower for the other part with the average speed being the product of the in-phase voltage and current. Thus measuring real power.
Yes. So how would the meter know which device has what amount of PF? It must do an equivalent resistance scenario for all the loads in the house with one common PF for the whole house and thus multiplying the voltage * current going into house * common PF. The meters can't judge individual PF of the devices.
__________________

You wouldn't want to see my tank. I don't use fancy equipment and I am a noob
Reply With Quote
  #10  
Old 03-07-2013, 07:03 PM
sphelps's Avatar
sphelps sphelps is offline
Member
 
Join Date: May 2006
Location: Lyalta, East of Calgary
Posts: 4,777
sphelps is on a distinguished road
Default

Quote:
Originally Posted by mrhasan View Post
Then my question is, how would each of the real power of individual components in the household be calculated by the utility meter?
Because the utility meter measures the exact same thing as the energy monitor, it measures actual power in kWh. It doesn't measure apparent power or vars.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 01:18 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.