Quote:
Originally Posted by wingedfish View Post
You won't fix it yourself unless you can understand what everything does. Before you had the AC installed the HRV was interconnected to your furnace/airhandler fan. The a/c guys tied into this same system. When your tstat calls for a/c, an inter connection in the tstat brings the air handler fan on also. What is happening to you is it is back feeding so when you turn on the HRV, the a/c turns on as well. This is very bad. To verify if i'm right, turn on your hrv and if the a/c is on, flip the fan switch on the tstat to "on". The a/c should turn off. At best it will cost a boat load of power. At worst it will ruin the compressor. Let the a/c guys know and they will likely fix it up for you.
Well you must be a HVAC installer as you were right. If the fan is going on the a/c unit after I turn on the Air exchanger and I turn the fan from auto to on, the fan does shut off. I am assuming this is a simple fix and it shouldn't cost me very much?