![]() Quote:
If you are going to run a new circuit (ie new wire from the breaker box) run wire rated for 40 amp to a subpannel close to your tank. then install three 15 amp breakers in the subpannel and run each one to a couple of outlets. A chiller doesn't need to be on its own breaker but if you got the room go for it. just make sure when you load up plugs you stay under 1500 watts on each 15 amp breaker ( I shoot for 1200 to 1300 on each breaker myself) or go by amps and put a max of 12 amps on each 15 amp breaker. this gives you room on the breakers. you chiller is 5 amps so you could run it on the same circuit as a few pumps and such. Put the lights on another ect.. Steve