#1
|
||||
|
||||
|
Just wondering whether 3 Son Agro 430 watt ballasts will fire up simultaneously on a single 15 amp circuit. I see that each ballast runs at 4.55 amps. That's 13.65 amps for the three. Will I require extra amperage at start-up or is the quoted amp draw for start-up.
Thanks, Andy |
|
#2
|
|||||
|
|||||
|
Depending on the brand of Son Agro, the start up is between 2 and 2.5 amps. but I think the problem would be running at almost 14 amps for a extended period of time.. that might be the iffy area.
Steve
__________________
*everything said above is just my opinion, and may or may not reflect the views of this BBS, its Operators, and its Members. If cornered on any “opinion” I post I will totally deny having ever said this in a Court of Law…Unless I am the right one*Some strive to be perfect.... I just strive. |
|
#3
|
|||||
|
|||||
|
I have found many 15A breakers will trip closer to 12A. You would also run it hot and it will then start to act up on you. I would go to a 20A to be safe. Your wiring must also be rated for 20A so don't just change the breaker, you could be starting a fire then.
Lee
__________________
Need more time for the tank... Break a leg! |