Yes this would make sence except he said this still happens when the t stat is switched off. Also I don't think most t stats jumper the y and g when in auto. I'm pretty sure the furnace board takes care of this. Or else when the fan switch was in off, and the t stat was in cool, the fan would not run. Sometimes on older furnaces without a y point people will jumper these points but op said thier was no jumper. The r and the rh need to be jumpered out unless you have a system with separate heating and cooling transformers. Which you don't. If the unit does not do this with the t stat wire disconnected at the bored then double check the t stat wiring and replace the t stat. I do not believe a relay is the way to go. I Hooked 2 of these up last week alone. The only way you should need a relay is if it is an older furnace with no y point.
Reply With Quote
  #2  
Old 04-30-2012, 01:44 PM
Seriak's Avatar
Seriak Seriak is offline
Member
 
Join Date: Jun 2002
Location: Calgary
Posts: 954
Seriak is on a distinguished road
Default

Quote:
Originally Posted by weyburnt View Post
Yes this would make sence except he said this still happens when the t stat is switched off. Also I don't think most t stats jumper the y and g when in auto. I'm pretty sure the furnace board takes care of this. Or else when the fan switch was in off, and the t stat was in cool, the fan would not run. Sometimes on older furnaces without a y point people will jumper these points but op said thier was no jumper. The r and the rh need to be jumpered out unless you have a system with separate heating and cooling transformers. Which you don't. If the unit does not do this with the t stat wire disconnected at the bored then double check the t stat wiring and replace the t stat. I do not believe a relay is the way to go. I Hooked 2 of these up last week alone. The only way you should need a relay is if it is an older furnace with no y point.
Which wire do you want me to disconnect from the tstat or do you want me to disconnect them all?
Reply With Quote
  #3  
Old 04-30-2012, 02:03 PM
wingedfish wingedfish is offline
Member
 
Join Date: Sep 2010
Location: Medicine Hat
Posts: 112
wingedfish is on a distinguished road
Default

Quote:
Originally Posted by weyburnt View Post
Yes this would make sence except he said this still happens when the t stat is switched off. Also I don't think most t stats jumper the y and g when in auto. I'm pretty sure the furnace board takes care of this.
If you have AC, try this on your furnace. Jump r to g at the furnace and no matter where the tstat mode is placed, if the fan switch is in auto, the AC will come on. It is a well known fact in the trade.

Quote:
Originally Posted by weyburnt View Post
Or else when the fan switch was in off, and the t stat was in cool, the fan would not run.
There is no off position for any fan switch on any thermostat.

Quote:
Originally Posted by weyburnt View Post
I do not believe a relay is the way to go.
You are wrong.
Reply With Quote
  #4  
Old 05-01-2012, 03:54 AM
weyburnt weyburnt is offline
Junior Member
 
Join Date: Feb 2012
Location: saskatchewan
Posts: 22
weyburnt is on a distinguished road
Default

I was suggesting to remove all t stat wires. If the problem still continues u know the backfeed is in the furnace board ie a jumper. If not the backfeed is in the t stat end. And if you jumper between r and g the furnace fan will come on. If you jumper from r to y then the Ac and furnace fan will come on. The exception is if you have an old furnace with no y. Then you would have to jumper between y and g on the t stat to force the Furnace fan on when T stat was calling for cool. This causes a problem because when the t stat was set to summer fan on, or hrv went to on the Ac would come on. As I said op says no jumper is installed. In that case a relay needs to be installed in order to remedy the problem. If I'm incorrect what would the y terminal be for. The y terminal allows the furnace fan to kick in when cooling is called but isolates the condenser contactor when the fan switch or hrv connects r and g. However op said this furnace has a y position on the board.

Op sorry to hijack your thread hope we are able to help, I know how frustrating things can get.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 06:24 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.