![]() |
|
Portal | PhotoPost Gallery | Register | Blogs | FAQ | Members List | Calendar | Search | Today's Posts | Mark Forums Read |
![]() |
|
Thread Tools | Display Modes |
|
#1
|
|||||
|
|||||
![]() Quote:
![]()
__________________
So many ideas, so little money! |
#2
|
||||
|
||||
![]() Quote:
It should have a trap, and probably it's own tie in. But the inspector saw it and passed me. I said it was a temporary installation. But is a trap all its missing? Easy to add, just didn't think it was needed since there is a trap in the floor drain.
__________________
-My 330g build thread |
#3
|
|||||
|
|||||
![]() I just know that Tony tried something similar here in Calgary and he ended up failing his inspection.
__________________
So many ideas, so little money! |
#4
|
|||||
|
|||||
![]() Wow, I got my whole plumbing permit failed because I had a sink draining into a floor drain like that (maybe I just had a big meanie of a plumbing inspector, or maybe Edmonton inspectors suck less than Calgary inspectors). I had to jackhammer the floor to tie into the main drain line AND tie the drain into the nearest vent to the ceiling. (And have a trap, but the main concern was that it didn't have it's own tie-in and venting) - apparently code only allows for "clear water" (aka furnace and A/C condensation) secondary drainage like that (I think that was the term he used for that anyhow) and anything else has to have a trap, tie-in and vent. (Pure awesome sauce.)
__________________
-- Tony My next hobby will be flooding my basement while repeatedly banging my head against a brick wall and tearing up $100 bills. Whee! |
#5
|
|||||
|
|||||
![]() This setup is fantastic.
![]() |
#6
|
||||
|
||||
![]() Quote:
I think he knew that so let it slide. Thanks, Still a work in progress, but getting closer. I need someone to come in and do a good cleaning. Lol. Sent from my GT-I9505 using Tapatalk
__________________
-My 330g build thread |
![]() |
Thread Tools | |
Display Modes | |
|
|