I was suggesting to remove all t stat wires. If the problem still continues u know the backfeed is in the furnace board ie a jumper. If not the backfeed is in the t stat end. And if you jumper between r and g the furnace fan will come on. If you jumper from r to y then the Ac and furnace fan will come on. The exception is if you have an old furnace with no y. Then you would have to jumper between y and g on the t stat to force the Furnace fan on when T stat was calling for cool. This causes a problem because when the t stat was set to summer fan on, or hrv went to on the Ac would come on. As I said op says no jumper is installed. In that case a relay needs to be installed in order to remedy the problem. If I'm incorrect what would the y terminal be for. The y terminal allows the furnace fan to kick in when cooling is called but isolates the condenser contactor when the fan switch or hrv connects r and g. However op said this furnace has a y position on the board.

Op sorry to hijack your thread hope we are able to help, I know how frustrating things can get.
Reply With Quote
 


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 01:59 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.