#1
|
||||
|
||||
![]() I have a gfci installed on the circuit which my tank is connected. I don't have afci's in my panel box and I am thinking I should install at least one on the circuit that my reef tank is connected. Like many people I've had my share of small and large spills luckily no salt water has reached the electrical source. An arc fault interupter would cut the power to the circuit before a fire could start. Who has installed these in their panels? Any electricians here to chime in about afci's?
|
#2
|
|||||
|
|||||
![]() Would a flood ever reach the height of your outlet? Or any exposed wiring where it would be immersed? If not, you may want to avoid the troubles AFCIs can cause with tripping.
Have you read this from Bean Animal's site? Pros and Cons; AFCI WHY NOT? Arc Fault Circuit Interrupters are designed to detect the electrical signature caused by electricity arcing someplace in the circuit. If arcing is detected, the AFCI breaker trips and removes power from the circuit. At first glance the AFCI appears to be a perfect candidate for fish tanks. Where there is water and electricity, there is a significant chance of arcing type fires. The problem is that AFCI breakers have a well deserved bad reputation for nuisance tripping when posed with a complex load such as a motor or ballast. An AFCI would add significant safety to a fish tank setup, but would also expose the livestock to a much higher greater risk of nuisance induced power outages. Most AFCI breakers also incorporate a GFCI into the device. A single GFCI used to power your tank (as mentioned above) is not a good idea. If you do not use AFCI circuit breakers (or the newer AFCI receptacles) then please take the precautions to prevent arcing type fires. That means taking precautions to protect power strips and other devices that will be exposed to moisture, drips and salt creep. |
#3
|
||||
|
||||
![]() Flood would not reach the height of the outlet. Spraying water is another possibility. I have the power bars high up and make drip loops. I had the front pane of glass of a 125 gallon break several years ago, when I found it water was spraying out through the crack. Had it been the back panel the outlets would have been very wet. Didn't think of nuisance outages I'm going to read up on them some more thanks.
|
#4
|
|||||
|
|||||
![]() I'm an electrician, and gfci detects the difference in current coming in on the hot wire and back on the neutral and they must be the same or it trips. That's why they're usednear sinks and stuff. And if you want the extra precaution raise your plugs to a satifying height. Or hardwire them. Use your imagination. Install a box in the wall cavity that has a door which will allow enough room for just your cords to passby and have some plugs inside the box.
|
#5
|
||||
|
||||
![]() Quote:
Installing AFCI is probably a good idea, but be ![]() Buy some good quality powerbars, plug them into GFCI receptacles and always use a drip loop in all your cords. |
#6
|
|||||
|
|||||
![]() Quote:
|