#1
|
|||||
|
|||||
![]() Hello all,
(ill apologize now to the moderators, if this is in the wrong spot) I am almost completed my fishroom, and have been installing external electrical to feed this room. I have a basic understanding of the household electrical, but i have a few questions that seem to have me stalled.... I wish to run a line out of my breaker panel,.. where i am wanting to draw this power from there exists an empty double pole breaker. (2x 15 amp) There is a pin connecting the two switches, so they only turn on or off together. My question is, if i run a single line (15 amp) out of there, using only one side of the breaker, does this have any effect on how that breaker pops if there is a problem ?. What would you change or is it ok that way? Heres #2, I have an existing armoured cable line running through the fish room, this line was exposed in the garage before the fishroom was built. This line has 3 wires (14-3?), it is also connected to a double pole breaker (2x15) also with a connecting pin. There are two Hot wires it appears, red and black each into its own side of the double pole.....with the white going to the nuetral bus. Does this mean this line is 220? What is making this confusing for me, is the only things this line is feeding is two unused outlets on another wall...wich are 110...?? Any thoughts on that are welcome and appreciated. Heres #3, There is another (pre-existing, but unused right now) cable that i intend to use for all my lighting. This line has 4 wires, and in the breaker box it appears the green is a ground, white again to the bus. The hots(red,black) are going to individual single pole 15 amp breakers. Is this intended for two individual lines, just being in one cable? Any thoughts would be welcome on the subject..as well on anyone who may be for hire to Pm me if interested in a small side job. Thank you, Marc.
__________________
Confucious say : Things that come to those who wait, will be things left over by those who didnt. |
#2
|
|||||
|
|||||
![]() 1. You could use the 2 x 15 amp breaker. If you only use one side of it it will still trip like normal. Chances are you will not need to use this though since you have 4 other circuits to use.
![]() 2. All this means is you have two seperate circuits both 110V. One being the red wire and the other being the black wire. They just happen to share the same neutral. If one circuit trips for some reason the other will as well because the breaker is connected. 3. This would be the same as number 2. Only difference being is that if one trips the other will not because the breakers are not connected. The green wire most likely is a ground. Check if it goes to a ground bar in the panel. Sounds like you will have lots of dedicated circuits for your fish room. Id come help you out but its a bit of a drive for me... ![]() |
#3
|
|||||
|
|||||
![]() I concur with Muck on this. The joined breakers are used for either split 110 receptacles, where each plug on the outlet is powered seperately as in a kitchen pluig, or for 220v use. The purpose is to ensure that if the breaker is tripped or shut down, both power sources, which go to the same location, are shut off for saftey reasons. Don't want to be opening a box to find there is another source of power there to suprise you. They can be used seperatly with no problem, ecept it could be a nuisance having both trip off together. The 14/3 cable is the lead that will power such an outlet. both can use the same neutral, so there is no need to run a pair of 14/2 wires. What I would do is switch that four lead wire onto the unused paired breaker for the above noted reasons, then use the individual ones for your new fish room circuits.
__________________
I retired and got a fixed income but it's broke. Ed _______________________________________ 50 gallon FOWLR, 10 gallon sump. 130 gallon reef, 20 gallon sump, 10 gallon refugium. 10 gallon quarantine. 60 gallon winter tank for pond fish. 300 gallon pond with waterfall. |
#4
|
|||||
|
|||||
![]() Quote:
Steve
__________________
![]() Some strive to be perfect.... I just strive. |
#5
|
|||||
|
|||||
![]() Quote:
220V Cable has 3 wires. Red and black which is your 220V Line to line and your ground. 110V (14/2) Cable has 3 wires white & Black which is your 110V Line to neutral and your ground. What Fudge has is definately (14/3) 110V wire on a split circuit. There are 4 wires: red, black and white and bare. Red to white makes circuit #1 @ 110V Black to white makes circuit #2 @ 110V and of course the ground wire. This wire (along with 2 threeway switches) is also often used when you are wiring in a light that can be controlled from 2 separate switches (ie top and bottom of stairs) Fudge ![]() hehe Just more wiring fun!!! ![]() ![]()
__________________
Gerald Home:160Gal. Foxface, Yellow Tang, Blue Tang, Coral Beauty, Lawnmower Blenny, Starwberry Dottyback, Mandarin Goby, 2 Percula Clowns, Green Brittle Star, Brown Brittle Star, Chocolate Chip Star, Cleaner Shrimp Store: 33Gal. Green Brittle Star, Chocolate Chip Star, Peppermint Shrimp |
#6
|
|||||
|
|||||
![]() Hey , Fudge , I am an Electrician
For get all other posts other than's MUCKs ,he has it right!
__________________
HAPPY REEF KEEPING !!______________________ |
#7
|
|||||
|
|||||
![]() Quote:
![]() |
#8
|
|||||
|
|||||
![]() Thanks Alot for the input guys !
I think i understand how Questions 1 and 3 work now. Ok, i think im getting this... It turns out both #2 and #3 questions cables have 4 wires total, red,black,white and a bare ground for the former, and red, black,white and green for the latter. So i am understanding these are identical except for the green wire instead of bare and i have a total of four circuits. Heres what i would like to do with Question #2`s cable, I am kinda gun-shy with this one, as it continues on into a wall and is lost to sight.... and im about 90% sure it is only feeding two standard 110 recepticles. I Have all Baseboard heating in the house, so i was scared this one may have been 220v feeding one or two...But, i cant find anything that stops working when this breaker is tripped except for the 2 plugs. Now, I have already split the line and was planning a junction there, in this junction, i was going to just feed a line of 4 recepticles on the fishroom side. Now If i get this correctly, It wont matter how its wired then downstream.(110 or 220) i can still tap into one of the hots(black or red) or both (for two individual circuits) and the whites...say, using the red and white to a recepticle or two, and likewise for black and white it will give me 1 or 2- 110v lines.... ![]() And is this a safe thing to do? (i like my house Un-charred ![]() Thanks again fellas,
__________________
Confucious say : Things that come to those who wait, will be things left over by those who didnt. |
#9
|
|||||
|
|||||
![]() Yes that sounds fine but if you don't use those other two plugs ( down the line as you said) I wouldn't bother reconecting them , to sort of make sure you don't over load the two 15 amp breakers . Ofcoarse I don't know how many pumps, lights,etc... that you are planning to have
__________________
HAPPY REEF KEEPING !!______________________ |
#10
|
|||||
|
|||||
![]() Hello All,
I tried wiring as you guys had stated, and all works fine.(if regular recepticles) Except i also tried installing GFCI`s to the first recepticle in each line, apparently they do not like sharing a common line(white)..they seen to trip as soon as i power it up. Any ideas ?
__________________
Confucious say : Things that come to those who wait, will be things left over by those who didnt. |