Tank Power
I just installed my gfci for my tank and found out that my tank shares a circuit with a lot of other receptacles plus some lights. How much power does a typical tank draw? Wonder if I am going to run into problems when everything is hooked up? :confused:
|
Quote:
|
One fuse will not handle a full blown reef and a bunch of household stuff as well. In general, it is far safer if the tank itself is split between two circuits so that if a fuse blows, some circulation (for instance) is still working.
|
Looks like I am just around 400w to run the tank. that includes lights(120w), return pump(31w), protein skimmer(20w), Powerheads(30w), ATO(5w), heaters(200w).
|
In terms of what your circuit can handle, watts is not a good unit to use as any device will be rated in true power rather than apparent. In other words depending on the power factor of the device the amount of power drawn into the circuit will be higher than what the actual device uses. Same goes if you use a kilowatt meter measuring watts. What you need to measure is volt-amps or just amps, especially for pumps as they often have low power factors, sometimes as low as 0.5 meaning they draw twice as much power as there rating.
House hold circuits are 15amps unless in the kitchen which newer homes will have 20amps circuits there. Easy to tell by looking at the outlets: http://www.diycontrols.com/images/15amp_20amp.JPG Safe load for a circuit is 80% capacity so for a 15 amp circuit you wouldn't want to exceed 12 amps total. So to find out if you're safe or not you'll need to add up all devices on the entire circuit, preferably in amps not watts. |
Quote:
Just track down every outlet that is also connected to the same fuse because you will want to avoid plugging in your vacuum cleaner, for instance, onto the same circuit. The big surge could be more than your tank circuit can handle. In our place, we have certain plugs that we can use for the vacuum and others that will blow the fuse, so I understand your concern. |
I've talked to several journeyman electricians and they've all said the same thing "if your not blowing your breaker than your fine". These guys have all been in the trade for many years, I trust them over any hobbyist.
|
Quote:
Also, ideally, if you have two pumps or wavemakers, have them on separate breakers so if something happens, the tank will still have circulation. It's not absolutely necessary but it is a good precaution. |
I will see what I can do. It looks like the whole wall is on the same breaker. If i run an extension cord across my living room I don't think my wife will be too happy.
|
Quote:
However, also as already mentioned, never a bad idea to split one or two critical components such as a heater or pump for your tank to another circuit. Not a problem if you're home, but if you're away & the circuit trips taking out all your tank components, your livestock might have a tough time surviving after a lengthy outage. A battery backup air pump or something would also help in that regard. |