So I am wondering if I should get a dedicated circuit for my 165G reef tank. Right now I estimate the wattage this thing would run continuously at 1500-1800W.
If so, could I make do with a 15A circuit or will I need a 20A. I know getting a 20A is the safe way, but I might not be able to easily so just want to know if 15 would be ok in all likelihood. |
A 15 amp breaker is only rated for 80% continuous, so 1200W. You need a 20A circuit. I have a dedicated 20A for my 150g.
With the 20A circuit, you need to run 12g wire as well. I actually ran 10g to mine, but I happened to have some lying around form a previous job. |
Quote:
|
BTW, I am an Electrician as well.. I should acctually be working right now, but the pull of Canreef is to much HAHAHA
Honestly Boss, I was programming the Logic Controller |
Quote:
Hey I thought I was the only one that posted a reply to his thread! Oops.. sorry I must have been typing when you posted your reply. All I know is I'm not a electrician or a plumber! :lol: |
imho I would rather have 2 15a cuircits, and split the load up.
not an electrician either, just a lineman.. |
Quote:
|
Quote:
|
Hmmmmm, ok sounds like I definitely gotta tackle this problem. I think I could potentially install a new 20 Amp circuit dedicated to the tank and have an extra outlet thats part of a 15 Amp circuit for the room as well for maybe some of the smaller equipment to be on.
What would you guys expect the charge to be to install a new dedicated 20 Amp circuit off my board and also switch out two outlets from regular ones to GFCIs. This would be maybe a 20 ft run of wire in an unfinished basement, so nothing major. Or could I cut costs by running everything myself and then just having the electrician do the connections? |
I bought a little book, "Alberta Electrical Code Simplified" at the hardware store when i first started fixing a few things in my last house. It has come in pretty handy to make sure I do things properly since i do not know the hundreds of pages in the electricians codebook.
I guess having an electrician check over your work before it was hooked up would be the same or better though. |
All times are GMT. The time now is 10:03 AM. |
Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.